[labnetwork] CDA and copper piping
Iulian Codreanu
codreanu at udel.edu
Thu Dec 8 08:47:59 EST 2022
Hi Kevin,
I've used cleaned-for-oxygen copper for CDA in two cleanrooms. Here at
UD I had a membrane dryer installed to lower the building supplied CDA's
dewpoint to -100F.
Cheers,
Iulian
iulian Codreanu, Ph.D.
Director, Nanofabrication Facility
University of Delaware
Harker ISE Lab, Room 163
221 Academy Street
Newark, DE 19716
302-831-2784
http://udnf.udel.edu
On 12/7/2022 8:32 PM, Matthew Moneck wrote:
>
> Hi Kevin,
>
> All of the mains and laterals for our -100F dewpoint compressed air
> are copper. We have not experienced any issues. If you have any
> concerns about particulate, you can install point of use filters, but
> have not needed to do so.
>
> Best Regards,
>
>
> Matt
>
> --
>
> *Matthew T. Moneck, Ph.D*
>
> Executive Director, Claire & John Bertucci Nanotechnology Laboratory
>
> Electrical & Computer Engineering | Carnegie Mellon University
>
> 5000 Forbes Avenue, Pittsburgh, PA 15213-3890
>
> Phone: 412-268-5430
>
> ece.cmu.edu <http://www.ece.cmu.edu/>
>
> nanofab.ece.cmu.edu <http://www.nanofab.ece.cmu.edu/>
>
> *From:* labnetwork <labnetwork-bounces at mtl.mit.edu> *On Behalf Of
> *Denis, Kevin L. (GSFC-5530)
> *Sent:* Wednesday, December 7, 2022 4:46 PM
> *To:* labnetwork at mtl.mit.edu
> *Subject:* [labnetwork] CDA and copper piping
>
> Hello All,
>
> Has anyone used copper piping for clean dry air lines. If not what
> kind of problems would one run into if going this route? Thanks for
> any insight that can be provided.
>
> Regards,
> Kevin
>
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://mtl.mit.edu/mailman/listinfo.cgi/labnetwork
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20221208/b3de4e56/attachment.html>
More information about the labnetwork
mailing list