    <div class="moz-cite-prefix">DITTO...ALWAYS 2...have your code
      consultant think life safety, not cost of dying.  While code may
      not require it (and I didn't see which code and interpretation was
      being referenced), codes are merely the MINIMUM needed, not what
      you would want for yourself or your people.<br>
      <br>
      The gas room in TMF's nanofabrication facility has 2 egress doors,
      one at each end.../DAB<br>
      <pre class="moz-signature" cols="80">David A. Bunzow
User Facilities Program Manager
The Molecular Foundry
Materials Science Division
Lawrence Berkeley National Laboratory
1 Cyclotron Road        MS 67-3207
Berkeley, CA   94720

Office:  510-486-4574
FAX:  510-486-7424
Cell:  510-542-1747
</pre>
      On 11/5/2012 1:21 PM, Weaver, John R wrote:<br>
    </div>
    <blockquote
cite="mid:6A848421F695C54A9210C1A873C96AC2068D1EEB@WPVEXCMBX04.purdue.lcl"
      type="cite">
      <pre wrap="">Always two! If you have a person working in the room and the incident happens between the person and the only exit, he/she is toast! I have doors at each end of my room so that no matter where the incident would occur there is a clear exit path from the room.

John R. Weaver
Facility Manager
Birck Nanotechnology Center
Purdue University
(765) 494-5494
<a class="moz-txt-link-abbreviated" href="mailto:jrweaver@purdue.edu">jrweaver@purdue.edu</a>


-----Original Message-----
From: <a class="moz-txt-link-abbreviated" href="mailto:labnetwork-bounces@mtl.mit.edu">labnetwork-bounces@mtl.mit.edu</a> [<a class="moz-txt-link-freetext" href="mailto:labnetwork-bounces@mtl.mit.edu">mailto:labnetwork-bounces@mtl.mit.edu</a>] On Behalf Of Iulian Codreanu
Sent: Monday, November 05, 2012 11:33 AM
To: Fab Network
Subject: [labnetwork] gas room means of egress

Dear Colleagues,

I am trying to influence a decision on a second means of egress from the gas room at the University of Delaware and your input is very much appreciated.

This is the room where the cabinets for toxic, flammable, and pyrophoric as well as some panels for inert gases will be located.  The room is adjacent to and separated from the cleanroom by a fire rated wall (I was told it is at least two hours-rated).  The code consultant states that a second means of egress is not needed for this H2 occupancy room but I feel it is a must.

How many doors does your gas room have?

Thank you very much.

Iulian
--
iulian Codreanu, Ph.D.
Director of Operations, UD Nanofab
University of Delaware

_______________________________________________
labnetwork mailing list
<a class="moz-txt-link-abbreviated" href="mailto:labnetwork@mtl.mit.edu">labnetwork@mtl.mit.edu</a>
<a class="moz-txt-link-freetext" href="https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork">https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork</a>

_______________________________________________
labnetwork mailing list
<a class="moz-txt-link-abbreviated" href="mailto:labnetwork@mtl.mit.edu">labnetwork@mtl.mit.edu</a>
<a class="moz-txt-link-freetext" href="https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork">https://www-mtl.mit.edu/mailman/listinfo.cgi/labnetwork</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>