[labnetwork] Combined or separate exhaust?
Massey, Travis
massey21 at llnl.gov
Sun Mar 2 20:45:34 EST 2025
Thanks to everyone who weighed in on this discussion! Apologies that I couldn’t respond to most of you directly.
I received many great pieces of advice that I’ll try (perhaps poorly) to summarize here:
1. A few people recommended this book<https://www.amazon.com/Semiconductor-Industry-Wafer-Exhaust-Management/dp/1574447203>. It does a fantastic job of detailing incompatible chemistries and various point of use and centralized devices for scrubbing/oxidizing/cracking/abating. It does not say much about material compatibility.
* Fun fact #1: LLNL got its first scrubber about a year ago!
2. The community is in broad agreement that it’s better to have dedicated exhaust systems for different chemistries, but very few actually are, because it’s expensive. Where labs are using >1 exhaust system, the +1 is typically for corrosives.
* Fun fact #2: LLNL has historically had 2 exhausts, one for fume hoods and one for tools and gas cabinets, with crosstalk between the two. Given this is largely the wrong setup, we’ve been lucky to not have problems in decades of history of this facility, likely owing to our high airflow and lower-than-most utilization. I’d prefer to do things right going forward, though!
3. I learned about fluoropolymer-coated stainless steel (e.g., PSP<https://www.fabtechinc.com/PS_PSP.php>) as a duct material. Expensive at time of installation, but the most versatile by far, especially if exhaust streams can’t be ideally segregated.
* SS, FRP, PVC, and galvanized steel each have their place. SS and galvanized steel are suitable for heat exhaust and solvents, with SS being the more premium option of the two.
* PVC and FRP are suitable for corrosives, with FRP being preferred for long runs and PVC suitable only for short runs from tool to trunk. However, FRP is reportedly the most difficult to work with, and few vendors are still using it.
4. There are different opinions on how important it is to separate (or scrub) the various different chemistries versus diluting them, and how severe the problems really are in a research-scale fab, but ammonia reacting with halogens to form salts is universally recognized as problematic.
* Fun fact #3: LLNL has had SC-1 and SC-2 at the same fume hood for a few decades. We’ll be investigating the ducts above the bench in the very near future for ammonium chloride deposits. Not to dismiss the concern, but my teammates (and more importantly, my predecessors) have never seen an airflow issue at this bench.
5. Most facilities have redundant fans. I’ve heard everything from 1+1 to 5+1. Universally considered good practice.
6. Several people referred me back to code and regulatory agencies. We’re under our emissions thresholds for Bay Area Air Quality Management District and California Air Resources Board, so no abatement has been required (yet). That said, I’ve been talking with those folks for a couple of months about better-than-minimum abatement with the expectation that requirements in the Bay Area will only grow stricter as time goes to infinity, and our utilization is expected to increase with time (and with this facility expansion).
Also, to the several folks to shared the wisdom to design with a long-term mindset, and to plan to do it right the first time – I’m 100% with you. With this fixed-budget expansion project, I would rather end up with a shell of a building that has all the right utilities in place but needs to be filled in over time with modular cleanrooms and last-mile utility drops, rather than to have a fully built cleanroom with inadequate utilities supplied to the building, improper materials/construction, or a 1/3 smaller footprint. I’m gradually getting the building folks to come around to the idea.
Best,
Travis
From: labnetwork <labnetwork-bounces at mtl.mit.edu> On Behalf Of Iulian Codreanu
Sent: Wednesday, February 26, 2025 5:03 AM
To: labnetwork at mtl.mit.edu
Subject: Re: [labnetwork] Combined or separate exhaust?
Hi Travis,
In the two cleanrooms I helped build I had a number of exhaust systems:
-Two for the cleanroom itself
-One for the gas room
-One for the gas bunker.
Each exhaust system has at least two fans for capacity and n+1 redundancy.
Folks use different names for the two exhaust systems typically used for the tools and hoods in cleanroom but a simple way to look at it is by focusing on the fume hoods:
-One is for corrosives; typically teflon-coated SS but I have plastic too (not my favorite)
-One is for solvents; typically SS but I have seen galvanized steel too (not my favorite)
When hooking up tools to the exhaust system you decide based on what kind of gases those tools will process; e.g. an evaporator ties to the solvent exhaust and a PECVD to the corrosive exhaust.
You have to keep in mind your local codes and the input of the authority having jurisdiction. EHS may be a good resource to support your efforts to perhaps go above the minimum requirements; when designing/building those labs my mindset was that I was going to live with them until I retired. We all know that it's easier/cheaper to put things in place when you build new rather than adding them later.
Good luck!
iulian Codreanu, Ph.D.
Director, Nanofabrication Facility
University of Delaware
Harker ISE Lab, Room 163
221 Academy Street
Newark, DE 19716
302-831-2784
https://udnf.udel.edu<https://urldefense.us/v3/__https:/udnf.udel.edu__;!!G2kpM7uM-TzIFchu!0QeMy7maqRVZHHc6rUqyhh1ejrXBvMCijTxVekBjc6JEoecHsRLqCrK7UpSTt18bM7CCf7SdeuRCcTz4nIyv$>
On 2/24/2025 9:23 PM, Massey, Travis wrote:
Hi all,
LLNL is planning a significant cleanroom expansion, and the question arose whether we need separate exhaust for hoods and tools/gases, or if they can be combined into a single shared exhaust. Or do you have a single exhaust with 2+ exhaust fans pulling simultaneously, so there’s always some exhaust air moving if one fan is down? The conventional wisdom around here has its share of holes, so I’m out to learn from the broader nanofab cleanroom community. How are your cleanrooms’ exhaust systems are configured, especially if you’ve had to go down this cleanroom design rabbit hole?
I’m also broadly open any other lessons learned regarding provisioning exhaust or other utilities – whatever you feel like sharing. Too much information during the design phase is far better than too little.
Thanks,
Travis Massey
Center for Micro and Nano Technology (CMNT)
Lawrence Livermore National Laboratory (LLNL)
_______________________________________________
labnetwork mailing list
labnetwork at mtl.mit.edu<mailto:labnetwork at mtl.mit.edu>
https://mtl.mit.edu/mailman/listinfo.cgi/labnetwork<https://urldefense.us/v3/__https:/mtl.mit.edu/mailman/listinfo.cgi/labnetwork__;!!G2kpM7uM-TzIFchu!0QeMy7maqRVZHHc6rUqyhh1ejrXBvMCijTxVekBjc6JEoecHsRLqCrK7UpSTt18bM7CCf7SdeuRCcSB_ZdvI$>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20250303/cdbbb52d/attachment.html>
More information about the labnetwork
mailing list