[labnetwork] wet bench EMO's

Matthew Moneck mmoneck at andrew.cmu.edu
Wed Apr 8 16:04:55 EDT 2026


Hi Kyle,

Our wet decks (manufactured by JST) only shut off 208V and 120V power to
the units.  DI, N2, and CDA feeds remain active, which means DI and N2
spray guns remain active, as well as purges for the electronics enclosures,
spinners, etc.  We also have CO2 fire suppression systems on all decks with
flammable solvents.  Those systems are powered by a separate panel
connected to building emergency power and will also remain active after
activation of the EMO button on the wet deck.

Best Regards,

Matt

On Tue, Apr 7, 2026 at 4:11 PM Kyle Keenan <kckeenan at seas.upenn.edu> wrote:

> Hello All,
>
> I'm curious to know what the EMO's do on the wet benches in your
> facilities. Do they shut down CDA, N2 or water, or just high voltage? What
> is the thought process behind what does/does not get shut down? We recently
> had a bad DI water leak on one of our benches, and we were a little
> surprised to find out that the EMO did not shut off the water supply, so we
> are considering whether or not we want to make a changes to the way the
> EMO's work on our benches.
>
> I look forward to reading your replies.
>
> Best,
> --
> Kyle Keenan
>
> Senior Manager - Laboratory Operations
> Quattrone Nanofabrication Facility
> University of Pennsylvania
> P: 215-898-7560
> F: 215-573-4925
>
> _______________________________________________
> labnetwork mailing list
> labnetwork at mtl.mit.edu
> https://mtl.mit.edu/mailman/listinfo.cgi/labnetwork
>


-- 

--
Matthew T. Moneck, Ph.D
Executive Director, Claire & John Bertucci Nanotechnology Laboratory
Electrical & Computer Engineering | Carnegie Mellon University
5000 Forbes Avenue, Pittsburgh, PA 15213-3890
Phone: 412-268-5430
ece.cmu.edu
nanofab.ece.cmu.edu
-------------- next part --------------