Alex,
In our building we maintain 21C ( I believe) and 42% RH. Temp is +/-1C, RH
+/-2%. Different processes are affected in different ways by these, so
control is the only way to ensure consistent results. For example,
photolith is very sensitive to RH, wet chemistry to temp.
We also move ~60000 cfm through the HEPAs.
Regards,
Garry J. Bordonaro
Microlithographic Engineer
Cornell NanoScale Facility
250 Duffield Hall
343 Campus Road
Ithaca NY 14853-2700
(607) 254-4936
<mailto:bordonaro at cnf.cornell.edu> bordonaro at cnf.cornell.edu
<http://www.cnf.cornell.edu/> http://www.cnf.cornell.edu/
Please acknowledge CNF in your publications:
"This work was performed in part at the Cornell NanoScale Science &
Technology Facility (CNF), a member of the National Nanotechnology
Coordinated Infrastructure (NNCI), which is supported by the National
Science Foundation (Grant NNCI-2025233)."
From: labnetwork <labnetwork-bounces at mtl.mit.edu> On Behalf Of Alex Dixon
Sent: Wednesday, December 17, 2025 12:12 PM
To: Lab Network <labnetwork at mtl.mit.edu>
Subject: [labnetwork] Cleanroom humidity
For those of you with climate controls in your cleanrooms, what relative
humidity do your keep your cleanroom at, and how tightly do you control the
fluccuations? How significant an effect have you seen on device
performance?
Our campus facilities is doing a climate control audit and asking any lab
with special requirements to justify them. Any info you could share would be
appreceated.
Thanks!
-Alex
__________________________________________________________
Alex Dixon, Ph.D. (He/Him)
Lab Manager
Nanofabrication and Thin Film Deposition
Shared Instrument Facility
Colorado School of Mines
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mtl.mit.edu/pipermail/labnetwork/attachments/20251217/aa5b9720/attachment.html>
More information about the labnetwork
mailing list